We built a house 7 years ago and it's insulated and has double glazing. I've installed Home Assistant with temp sensors in the bed rooms and seeing 70%+ humidity levels. Temperature is always above 16c

We ventilate it, but still it's 70% in the bedrooms. WHO recommends 40-60%, so we're a bit worried.

Living room is around 55% during the day when we have the heat pump set at 21c.

As it's pretty humid outside I think it's almost impossible to get it lower, but are there any other tips? I don't want to run dehumidifiers. Would an HRV like system help?

top 50 comments
sorted by: hot top controversial new old
[–] [email protected] 8 points 1 year ago (1 children)

So your house is insulated and warm, and presumably pretty sealed. I think you should be considering sources of water vapour.

Some common sources:

  • Shower
  • Drying clothes inside
  • Cooking

If you have a separate shower (rather than shower over bath) you can get a shower dome which significantly reduces steam leaking outside the shower. I don't much like using a shower with one but they are effective. You can also get a more powerful extractor fan, though even the super powerful ones don't seem to be that powerful (I want one that sucks your clothes off).

If you dry clothes inside, try not to. If you have a dryer that isn't a condenser dryer, try to vent it outside or at least open the window. Probably try to use it less though using it less and not drying clothes inside don't make for many options in the winter.

For cooking, make sure you have a rangehood to catch the steam from any boiling pots. And make sure it's externally vented. I have lived in placed with rangehoods that just push the air back into the room (I'm not sure of the point...) but I'd think with a house that new it wouldn't be an issue.

You might have other ideas about sources of water. Gas heaters can be one but it sounds like you heat with a heat pump.

An HRV/DVS can help but I'm not sure it's as effective in a newer house.

You also mention the living room is 55% in the day when heated to 21c, what temperature are the bedrooms when they are 70%? Colder air can hold less water, and so the relative humidity is higher with the same amount of water in the air.

[–] [email protected] 4 points 1 year ago (2 children)

Thanks Dave, much appreciated! Yes, I guess it's from internal sources, like shower, drying clothes and cooking. Will try to decrease that, but as you said, drying clothes outside is not really an option in winter.

So, right now, living room is [email protected]%. Bed room 1 is [email protected], bed room 2 is [email protected]%, bed room 3 is [email protected]% We've got doors open so it should stabilize a bit more. I understand that higher temps means lower RH, but I don't want to heat bed rooms to 21c. There are panel heaters in each bed room, which are set at 16c during the night, and at 19c at the end of afternoon until 6pm.

Garage is [email protected]; which is not insulated & not heated.

Think as a gap stop I'll get a dehumidifier, especially for the colder winter months.

[–] [email protected] 5 points 1 year ago (2 children)

Other than the garage, those temperatures/humidities all have a similar amount of moisture in the air, the difference comes from the temperature of the room. See this calculator I googled up: https://www.omnicalculator.com/physics/absolute-humidity

So the warm air has X amount of water in it, and when it goes to the cold room it still has the same amount of water, but because cold air can hold less water the relative humidity goes up. So I don't think there's anything special about the bedrooms.

The dehumidifier is probably a good idea, but before you go and buy one, check if your heat pump has a "dry" setting.

[–] [email protected] 4 points 1 year ago (4 children)

Thanks Dave again for the insights!

Our heat pump has a dry setting, but it must be set 2c lower than ambient temperature. So it's getting quite cold. I was hoping / assuming that a dehumidifier wouldn't cool that much.

But perhaps worth giving it a try for an hour or so.

[–] [email protected] 5 points 1 year ago (3 children)

Ah interesting, I've never read the instructions just hit "Dry"!

Don't forget to warm the room back up before checking the humidity or the cooler air might make you think it hasn't made a difference :).

On another note, I've always wanted to try home assistant but never got around to actually getting any equipment. What sensors did you get?

[–] [email protected] 4 points 1 year ago (1 children)

Don’t forget to warm the room back up before checking the humidity or the cooler air might make you think it hasn’t made a difference :).

Yes good point! Doing a test now, set to dry, will check how it goes.

On another note, I’ve always wanted to try home assistant but never got around to actually getting any equipment. What sensors did you get?

First of all, it can be a rabbit hole. Secondly, it's awesome. I've set it up on a Raspberry Pi, and set up a Zigbee mesh with the Home Assistant SkyConnect dongle from here. I bought some Sonoff temp sensors, and Sonoff Smart Sockets to increase the Zigbee network range. I've also bought some Smart Sonoff Bulbs at Aliexpress but I'm not very happy with them as they caused some Zigbee network issues. Seems to have resolved it by itself somehow.

Our heat pump is not a smart one, so I'm using a Broadlink RM3 Mini to control my heat pump. Works like a charm. That way I would also be able to set it to dry and heat on intervals of e.g. 1 hour during the night.

Any other questions just ask.

[–] [email protected] 3 points 1 year ago (6 children)

Oh boy, that's cheaper than I was expecting startup costs to be... I am oh so tempted now!

With HomeAssistant, as I understand it, it needs the full Pi? I have a bunch of services running on my RPi 4 and so when I've looked at HomeAssistant I haven't been able to install this without touching the other stuff on there. I think they have a docker container version but it has a lot less features.

I have for a while been intending to uprade my stuff to something that can handle photos/videos better, but haven't got around to it. I might need to wait until I do that, then I'll have a spare Pi to use for HA.

I'm guessing an RPi 1B won't handle it. It's running Pi hole at the moment, but I think this is about the only thing it's capable of.

[–] [email protected] 2 points 1 year ago (6 children)

With HomeAssistant, as I understand it, it needs the full Pi? I have a bunch of services running on my RPi 4 and so when I’ve looked at HomeAssistant I haven’t been able to install this without touching the other stuff on there. I think they have a docker container version but it has a lot less features.

I'm running it dockerized as well as I'm using it for other stuff as well, like PiHole, media server, etc. No problems at all.

Some features are missing, like editing config files in the browser. Major gap is that add-ons are not supported. Add-ons are essentially 3rd party apps, like DuckDNS, Frigate or MQTT. It's mostly annoying because the documentation assumes you run the HASS version. But it's no big deal, you can set up those apps yourself. I'm running Frigate and MQTT dockerized and connected to HA without issues.

For docker resources, check out https://www.linuxserver.io/. I used to install apps like NZBGet, Radarr, etc. all directly, which was very annoying as each app uses a different install script. With the docker compose files from linuxserver it was a breeze. I only run PiHole directly, as I saw some issues with the Docker version, the rest is all dockerized.

load more comments (6 replies)
[–] [email protected] 2 points 1 year ago (12 children)

I have for a while been intending to uprade my stuff to something that can handle photos/videos better, but haven’t got around to it. I might need to wait until I do that, then I’ll have a spare Pi to use for HA.

I’m guessing an RPi 1B won’t handle it. It’s running Pi hole at the moment, but I think this is about the only thing it’s capable of.

Not sure, HA itself is not very demanding. Most demanding thing I'm running are NZB's (extracting / par check), Photoview (to index the photos on my NAS), and Frigate (web cams with motion detection). I've set CPU limits for each docker container to ensure it's not overloaded, installed a fan, and now it seems to perform okay.

load more comments (12 replies)
load more comments (4 replies)
[–] [email protected] 3 points 1 year ago (1 children)

I'm seeing some odd behaviour. I've set the heat pump to dry twice, for about 30 minutes. Both temp and RH drop, which is good. However, as soon as I turn it back to heat, the RH jumps up about 6% within 5-10 minutes. The sensor is a couple of meters away from the heat pump, so that's odd.

Also outside it's 14.5c @ 72% so I have no idea how to get it 16c and below 60%. That seems only possible if I shut all windows and have dehumidifiers running 24/7. I see articles where they recommend 30-50% in winter, how the heck is that possible when it's damp outside.

[–] [email protected] 2 points 1 year ago (2 children)

I’m seeing some odd behaviour. I’ve set the heat pump to dry twice, for about 30 minutes. Both temp and RH drop, which is good. However, as soon as I turn it back to heat, the RH jumps up about 6% within 5-10 minutes. The sensor is a couple of meters away from the heat pump, so that’s odd.

Could this be as simple as the heat pump is blowing out dry air, but hasn't turned over much air total. Then when you stop it, the dry air mixes with other air around the house and the humidity comes back up?

Also outside it’s 14.5c @ 72% so I have no idea how to get it 16c and below 60%. That seems only possible if I shut all windows and have dehumidifiers running 24/7. I see articles where they recommend 30-50% in winter, how the heck is that possible when it’s damp outside.

I dunno man. I tend to think I live in a warm, dry house. We only heat rooms we are using but otherwise we don't hesitate to turn on a heat pump. We have never had an issue with mould or dampness. But I just have this feeling when I get some sensors they are gonna say 70% like yours and I'm gonna have to go down a rabbit hole trying to work out why!

We do have a DVS, but ours is an older home. I think they help more with heat recovery (all they do is pump air from your ceiling cavity into your house - which is often warmer because heat rises). They do slightly pressurise the house because they are pumping air in, which can help stop outside air getting in cracks, but I can't imagine a fairly new house like yours would have the same issue with that as our 50's house. Maybe throw a sensor in the ceiling and see if the air is warm and dry up there?

[–] [email protected] 3 points 1 year ago

I think your assessment is likely correct, 30 minutes isn't long for a dehumidifier to do much work, and unless there's a unit in each room, or its central then for the total volume of air it won't have pulled much more than was in the general area its located.

[–] [email protected] 2 points 1 year ago (1 children)

Yeah we assumed our house wouldn't have moisture issues being so new. But... If I hadn't measured I wouldn't know as we don't have massive moisture issues. Main issue is condensation on the window frames as they are not thermally broken. Well it is what it is.

I've ordered a 10L dehumidifier, we'll ventilate more, and let's see how it goes then.

It's not so easy to get onto the ceiling but it's indeed worthwhile.

[–] [email protected] 2 points 1 year ago

Good luck!

It’s not so easy to get onto the ceiling but it’s indeed worthwhile.

You don't have a man-hole in the ceiling in a wardrobe/laundry or other out of the way place where you can just poke a sensor up into the ceiling?

[–] [email protected] 2 points 1 year ago (16 children)

Ah interesting, I’ve never read the instructions just hit “Dry”!

Yeah, I noticed it didn't do anything when set to e.g. 22c when it was already 22c there. Then I read the manual, which is a bit cryptical:

When the room temperature is higher than the temperature setting: The device will dehumidify the room, reducing the room temperature to the preset level. When the room temperature is lower than the temperature setting: Dehumidifying will be performed at the temperature setting slightly lower than the current room temperature, regardless of the temperature setting. The function will stop (the indoor unit will stop emitting air) as soon as the room temperature becomes lower than the setting temperature.

Notice the bold part. First it says, if the temp setting is higher/same as ambient, it will perform slightly below ambient. However, next sentence it says it stops when temp setting is higher/same as ambient?

I have to set it e.g. 2c lower than ambient, otherwise it just doesn't do anything

load more comments (16 replies)
load more comments (3 replies)
[–] [email protected] 2 points 1 year ago (1 children)

So many folks overlook the Dry setting on a heatpump :)

load more comments (1 replies)
[–] [email protected] 2 points 1 year ago

You could probably solve most of this problem by installing an ERV but those are fairly expensive.

[–] [email protected] 8 points 1 year ago* (last edited 1 year ago) (1 children)

What do you mean exactly you ventilating. Mechanical ventilation?

Modern houses NEED mechanical ventilation. It's a travesty that new houses in NZ don't come with mechanical ventilation as standard, as is done in the rest of the developed world.

It's pretty obvious if you think about it. Seal the house well, well insulated, double glazed. How will the moisture leave without ventilation. This is why modern houses NEED mechanical ventilation. Older houses don't need mechanical ventilation because the house is already leaky.

And not the silly DVS thing. I don't want rat infested air from my attic thank you. I don't care how good the filters are. Ventilation from the outside please.

What this looks like is intake vents in the soffit, a duct, and fan that pumps fresh air in for positive ventilation. Our you can do negative pressure where it pumps out, or balanced where you have air coming both in and out. You can install a mechanical heat recovery system if the house gets cold.

Full HVAC includes ducted heating/cooling.

TLDR: your house is humid because it's well sealed and the builders couldn't be bothered putting in mechanical ventilation because we are 20 years behind the rest of the world.

If you already have mechanical ventilation then it is likely not installed properly. Just putting it in doesn't necessarily mean it's sized correctly for example.

[–] [email protected] 5 points 1 year ago (7 children)

What do you mean exactly you ventilating. Mechanical ventilation?

We've got mechanical ventilation in the bathrooms.

But I meant just old school opening all the windows :)

TLDR: your house is humid because it’s well sealed and the builders couldn’t be bothered putting in mechanical ventilation because we are 20 years behind the rest of the world.

Yes, I understand that, we generate moist from cooking/breathing/washing and that has to go somewhere. We've got many windows open a little bit 24/7.

I'm from Europe, and yes, houses are better insulated, we had double glazing 30 years ago, and now have triple glazing, but ventilation was never an issue. We just open our windows to ventilate for e.g. an hour and that's it.

[–] [email protected] 2 points 1 year ago (1 children)

Thanks for further details. I would definitely invest in getting HVAC installed in that instance or if cost is an issue then at minimum install simple positive pressure mechanical ventilation from the outside into the bedrooms. This should fix your problem. It sounds like windows aren't enough because the house is well sealed, so you need a mechanical solution. Please don't get DVS from the attic.

I live in a new house with HVAC and leave the mechanical ventilation on when not heating or cooling and it keeps moisture levels low. I also got HVAC retrofitted into my previous house which made a massive difference in moisture. I'll never live in a house without HVAC in the future if I can help it.

[–] [email protected] 3 points 1 year ago (1 children)

We do have HVAC, in a heat pump. It's running all day. A complete system like HRV is a bit too much for now. The dry setting is annoying as it is cooling. Not handy mid winter.

[–] [email protected] 2 points 1 year ago (1 children)

You mean a split system? A heat pump usually refers to a split system which doesn't have the V in HVAC as it just recirculates air. HRV is the ventilation from the attic thing, please don't get that.

HVAC generally refers to ducted aircon with mechanical ventilation. The "heat pump" sits in the attic. Fresh air is taken in from the outside through the soffit. Ducts run from the "heat pump" into each room.

If a ducted system is too expensive then you should install plain mechanical positive pressure ventilation from the outside (not HRV/DVS) Depending on your house it is possible to DIY this using stuff from Bunnings. You could even link the fan to your Home Assistant and get it to activate when the humidity reaches a certain threshold. This should fix your problem. If it causes the house to get cold by doing this then you could install a mechanical heat recovery device.

[–] [email protected] 3 points 1 year ago (1 children)

Thanks mate, that is very useful. Yes, we indeed only have a heat pump.

I looked into HRV/DVS alternatives some time ago, and Cleanaire was recommended on e.g. Geekzone; which gets the air from outside & heats it. Quote was $4-5k which is a bit steep as we're not sure how long we'll be living here.

A DIY option for a PIV isn't too bad. I could leave it running overnight and use the heat pump to keep the house above 16c.

I also bought a small dehumidifier as a stop gap.

I've left the heat pump running on dry / heat cycles overnight (1 hour dry to 17c, 1 hour heat to 19c). Didn't do anything, RH at the end was exactly the same as the night before.

[–] [email protected] 3 points 1 year ago (9 children)

Oh wow mechanical heat recovery systems have jumped in price. They were 2-3k a few years ago. The way mechanical heat recovery works is kind of like penguin legs. The inflow and exhaust airflows pass by each other. So the warm exhaust air passively heats the cooler inflow air. So they are quite basic things that are very cheap to run. I guess another kiwi tax. Done some googling for pricing and it does appear 5-6k is the going rate now. E.g. another option: https://www.smooth-air.co.nz/home/hex390

What about something like this: https://www.smartvent.co.nz/why-smartvent/ that should also improve the humidity. Doesn't say price though. They seem to have a variety of options including positive pressure which should be much cheaper than a heat recovery system. https://www.smartvent.co.nz/smartvent-positive-advance/

Here's some more information about heat recovery systems and why DVS/HRV from the attic are shit. https://www.smarterhomes.org.nz/smart-guides/heating-cooling-and-insulation/ventilation-and-heat-recovery-systems/

[–] [email protected] 2 points 1 year ago

Thanks for the details!

Smooth air has kits for just ventilation for 1.5k for 2 rooms. Smartvent is more expensive, like 4k, they have some pricing.

I don't need a lot of bells and whistles. I can automate it myself. Just an outdoor outlet and an indoor outlet, ventilator and two pipes for just the living room.

I read your article, they say HRV/DVS is bad for heating, but not if you use it just for ventilation?

One other easier option is to just have a simple diy DVS by using the air from the attic. I'm going to check the moisture levels there first.

load more comments (8 replies)
load more comments (6 replies)
[–] [email protected] 4 points 1 year ago (1 children)

70% you need to be running dehumidifiers...

It's not just mold that's an issue, it can cause structural damage.

[–] [email protected] 3 points 1 year ago (1 children)

As I understand it, dehumidifiers are not a proper long term solution for an entire house; they are recommended for rooms where ventilation is hard.

[–] [email protected] 4 points 1 year ago (1 children)

You can call an HVAC specialist and get something more permanent, but you need to do something ASAP.

But you can absolutely get one with a drainage tube and run it 24/7 tho. Lots of people in older houses in America do it.

[–] [email protected] 3 points 1 year ago (3 children)

Thanks. You mean a dehumidifier with a drain tube? I haven't seen one here in NZ.

[–] [email protected] 2 points 1 year ago

Makita sell a handy tool that can fix that 🤣

load more comments (2 replies)
[–] [email protected] 3 points 1 year ago (1 children)

Vapour barrier. Vapour barrier. And maybe a vapour barrier.

They're really cheap and only a little difficult to install. I've installed them in every house I've ever lived in. In our current house things dried out so much some of our floorboards warped a little. They are magic.

[–] [email protected] 3 points 1 year ago (2 children)

Never heard of that, thanks. Our house is built on a concrete slab, so don't think that will work?

[–] [email protected] 2 points 1 year ago

If there's an air-gap between the slab and your floor, and you can get in there, then yeah it will help. Concrete is remarkably porous to water.

load more comments (1 replies)